    I know this isn't a house forum, but I could really use some help. I have two young girls and can't afford to have my house so hot. I tried calling and should have someone out on Fri/Saturday. Okay, here goes the novel...

    I have an outdoor A/C unit, new attic unit and all new ducting along with a digital thermostat put in about 2 1/2 years ago. Been trying to change the filters about every 30-60 days along with running some bleach down the overflow to keep it from backing up.

    within the past two weeks I've been noticing that the digital thermostat will be set at a temp, but the actual temp it's reading is much higher (set to 73 actual temp 78-79 and climbing. I have a newborn and probably haven't changed the filters in three months. The guy told me that filter was probably dirty causing the attic condensor to freeze up. He said to turn off the unit and run the fan on "ON" for an hour or so, then try to turn the Air conditioner back on.

    So I turn it off and just run the fan. The house starts to cool off which I thought might be due to the freezing coil thawing? I fell asleep and woke up the next morning to a house that was 68 degrees with the A/C off and only fan set to on. this happened again yesterday and once again, this morning it was 68 again. tonight when I got home, yep 79 degrees again.

    Does anybody know what would cause the unit to be cooling the house when the a/c is set to off an the fans are set to manual on? I noticed that both the attic vent fan and then outside blower are both running when I have it on Manual On fan. Could this be something with the digital thermostat?

  2. #2
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    its the thermostat most likely, i have put some on and the next day they are bad. what kind of stat is it man? a programable stat? or just one with the options of heat/cool then fan-on/auto?

  3. #3
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    or could simply be the anticipator setting on the stat which might be off also.

    is the outside compressor running when cool is off? and you just have the fan set to on?

  4. #4
    Something Diabolical... chuckie669's Avatar
    Join Date
    May 2007
    Location
    Houston, Texas
    Posts
    2,677
    2000 C5 Torch Red

    It's programmable. Pic just taken below. sofar it's dropped one degree.

    EDIT: wow, that was a shitty pic...

  5. #5
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    there is a possibility that someone messed with the settings? kind sounds that way to me. so set it to off and the fan on auto what does it do? does the compressor run still to the outside unit?

  6. #6
    Something Diabolical... chuckie669's Avatar
    Join Date
    May 2007
    Location
    Houston, Texas
    Posts
    2,677
    2000 C5 Torch Red

    Quote Originally Posted by Zboner View Post
    or could simply be the anticipator setting on the stat which might be off also.

    is the outside compressor running when cool is off? and you just have the fan set to on?
    Yes, the outside unit is running and the fan out there is blowing warm air. Up in the attic there is also a fan blowing, which I'm guessing vents out to the roof?

  7. #7
    Something Diabolical... chuckie669's Avatar
    Join Date
    May 2007
    Location
    Houston, Texas
    Posts
    2,677
    2000 C5 Torch Red

    Quote Originally Posted by Zboner View Post
    there is a possibility that someone messed with the settings? kind sounds that way to me. so set it to off and the fan on auto what does it do? does the compressor run still to the outside unit?
    Changed the fan to auto and left the ac off. After about a minute, I heard the suction cut off on the filter and walked outside. Outside unit was off also.

  8. #8
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    ok well just try and switch it with the fan on auto and the setting to cool, also you can use your programable stat just like a normal thermostat and you dont have to fool with all the settings.

  9. #9
    11 years of bangin gears cammed goat's Avatar
    Join Date
    Jan 2009
    Location
    North Jersey
    Posts
    11,496

    Phantom Black Metallic
    2004 GTO M6

    Man, I wish I could remember my HVAC apprenticeship days.

  10. #10
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    Quote Originally Posted by chuckie669 View Post
    Yes, the outside unit is running and the fan out there is blowing warm air. Up in the attic there is also a fan blowing, which I'm guessing vents out to the roof?

    im sure up stairs you have 2 pvc pipes running out the roof or the side? or do you have a heatpump? if you have a heat pump your main source for heat/cool is from the outside unit.

    is the big copper line cold?

  11. #11
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    Quote Originally Posted by cammed goat View Post
    Man, I wish I could remember my HVAC apprenticeship days.

    lol, been there and do it every day even though i dont have my license still

  12. #12
    Junior Member
    Join Date
    May 2007
    Location
    Wilmington DE
    Posts
    5

    Pewter
    1998 Corvette

    Hey Chuckie, I'm an hvac service tech and it sounds like your evaporator coil in the attic may be freezing up due to a low freon charge. Have someone check the charge in the a/c system. If it freezes up it won't cool the house and when you shut it off it will melt the ice. Combine that with the cooler night temps and it will drop the house temp. During the day it can't keep up because the charge is low, and that will freeze up an evaporator coil.

  13. #13
    Something Diabolical... chuckie669's Avatar
    Join Date
    May 2007
    Location
    Houston, Texas
    Posts
    2,677
    2000 C5 Torch Red

    Quote Originally Posted by Zboner View Post
    im sure up stairs you have 2 pvc pipes running out the roof or the side? or do you have a heatpump? if you have a heat pump your main source for heat/cool is from the outside unit.

    is the big copper line cold?
    Line was cold. I keep the ac set to cold and the fan to auto. It gets warmer. I just set it back to off and fan on, and can seriously feel cooler air coming out of the vent. I also tried replacing the battery in the thermostat and can't tell any difference.

  14. #14
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    yea the battery in the stat is nothing it is getting 24volts from the furnace, dude ok it sounds like its the stat i would honestly start there and if its not the stat its the board which is expensive as hell, but you said its a new furnace you should have a 3 year warrenty on parts all you have to do is pay for labor.

    if i was closer i would run down and try and figure it out, i just put in an a/c unit friday man.

  15. #15
    11 years of bangin gears cammed goat's Avatar
    Join Date
    Jan 2009
    Location
    North Jersey
    Posts
    11,496

    Phantom Black Metallic
    2004 GTO M6

    Quote Originally Posted by Zboner View Post
    lol, been there and do it every day even though i dont have my license still
    That sh1t was fun...the layoffs...not so much.

  16. #16
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    Quote Originally Posted by chuckie669 View Post
    Line was cold. I keep the ac set to cold and the fan to auto. It gets warmer. I just set it back to off and fan on, and can seriously feel cooler air coming out of the vent. I also tried replacing the battery in the thermostat and can't tell any difference.

    ok do you have a heatpump? well are you all electric? no gas? if so the reversing valve could be taking a dump on you.

  17. #17
    Senior Member Zboner's Avatar
    Join Date
    Aug 2005
    Location
    cincinnati/northern ky
    Age
    37
    Posts
    9,035

    Black
    99 SS

    Quote Originally Posted by cammed goat View Post
    That sh1t was fun...the layoffs...not so much.

    yup but side work is bad ass, i just put in a new outdoor unit and indoor a coil last weekend and only charged the dude 2,500 for it, hell materials was only like 1,200 so i made bout 1,300 on it in 5 hours. win win for both of us.

  18. #18
    11 years of bangin gears cammed goat's Avatar
    Join Date
    Jan 2009
    Location
    North Jersey
    Posts
    11,496

    Phantom Black Metallic
    2004 GTO M6

    Quote Originally Posted by Zboner View Post
    yup but side work is bad ass, i just put in a new outdoor unit and indoor a coil last weekend and only charged the dude 2,500 for it, hell materials was only like 1,200 so i made bout 1,300 on it in 5 hours. win win for both of us.
    That IS good. It's like a puzzle. Put all the pieces together and connect the wires. Then the moment of truth: flicking the switch and hearing the whirrr of the unit coming to life. Total win right there. Was quite gratifying.

  19. #19
    Something Diabolical... chuckie669's Avatar
    Join Date
    May 2007
    Location
    Houston, Texas
    Posts
    2,677
    2000 C5 Torch Red

    I think it's gas/electric. I do have a gas line that runs to it in the attic, but can't tell you for sure if it's just for the furnace.

    I've had the fan running for a few hours now and still 77 in the house. i'm going to set the a/c back to 74 and fans to auto and crash for the night. Guess I'll see if it keeps cooling down tonight.

    The part of the puzzle that I hate is where everything looks like it works, but doesn't.

    Thanks Zboner

  20. #20
    Veteran 0rion's Avatar
    Join Date
    Aug 2005
    Location
    ohio
    Posts
    22,554

    98 Formula
    06 duramax

    t-stat's are cheap. I would get rid of that digital stat and just go with a regular t-stat for $14 or whatever they cost. I'm no a/c guy but I've worked on my POS more than once. Might just try swapping that stat and see if that works.....cheap test and they're easy to install.

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. home security guru's ....step inside...
    By jiveass in forum Almost Anything Goes
    Replies: 12
    Last Post: 09-20-2011, 04:55 PM
  2. Computer guru's... Help/info needed
    By OreoLt1 in forum Computers / Gaming
    Replies: 12
    Last Post: 02-15-2011, 09:45 PM
  3. 12 Bolt Guru's... Assistance Needed
    By ebdboudreaux in forum Drivetrain
    Replies: 5
    Last Post: 04-10-2009, 02:08 PM
  4. Computer guru's needed, DSL question
    By CaptainCaveMan in forum Almost Anything Goes
    Replies: 11
    Last Post: 02-17-2006, 12:05 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •