    Got a home DIY question - electrical related

    for the DIY'ers on here,..

    i've got a single gang GFCI recepticle in my garage, it's on a 15A circuit. there are some other things on this circuit: a light (switched) in the utility closet, two overhead lights (switched) on the ceiling, an outdoor recepticle on the side of the house.. i think that's it. so i count the "equivalent" of 5 receptacles, counting the GCFI recepticle..

    so what i want to do is cutout the box w/ the GFCI recepticle and put in either a two gang or three gang box, so i can have more indoor recepticles (i.e. more than one). BTW, one of the new recepticles i can put in is a combo switch, so i can plug my under-cabinet/task lighting into it.

    so, does anyone know if NEC (Edit: sorry not NEMA) specifies a limit on the number of recepticles you can put on a 15A GFCI circuit. if i go to a three gang box, my total "equivalent" number of loads on the circuit would be 7. also, any problem w/ putting the GFCI recepticle in the same box as one or two other recepticles (2-gang, or 3-gang)?

    Last edited by wileyCoyote; 06-26-2011 at 10:32 AM.

  2. #2
    Bone it like you own it FORD RECOVERY EXPERT's Avatar
    Join Date
    Sep 2005
    Location
    TEXAS... U mad?
    Posts
    6,158

    Black / Stryker Blue
    2K WS.6/ 2K9 G8GT


  3. #3
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    yeah, i've read in others online posts/forums about a power (volt-amp) rule to figuring this, ..but then someone on there was saying that didn't apply to residential.. someone else saying that there is no "limit" per se, on the number of receptacles you can have on the circuit.??

    15Ax120V = 1800VA (circuit capacity)

    90VA per load, 180VA per duplex receptacle.

    so for me, currently

    GFCI (duplex): 180VA
    light in utility room: 90VA
    overhead lights : 90VA x 2 = 180VA
    outdoor recepticle (duplex) : 180VA

    total = 630.

    so that means i have some elbow room here? ... so confusing!..

  4. #4
    Member BrntWS6's Avatar
    Join Date
    Oct 2005
    Location
    Land of the FOID
    Posts
    330

    SOM
    2002 WS6 M6 - 461hp 406tq

    Some municipalities limit the number of receps on one circuit per there local addendum's (usually 10) but if your not pulling a permit don't worry about it. There is no problem putting a GFCI in with other devices.

    If your worried about overloading your circuit just add up total wattage of whatever you have plugged in and your lights and divide by 120v to get amps. Don't exceed 80% of total load. So a 15amp circuit you wouldn't want to go over 12amps.

    Just make sure all outlets (not switches or lights) are GFCI protected.

  5. #5
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    Quote Originally Posted by BrntWS6 View Post
    Some municipalities limit the number of receps on one circuit per there local addendum's (usually 10) but if your not pulling a permit don't worry about it. There is no problem putting a GFCI in with other devices.

    If your worried about overloading your circuit just add up total wattage of whatever you have plugged in and your lights and divide by 120v to get amps. Don't exceed 80% of total load. So a 15amp circuit you wouldn't want to go over 12amps.

    Just make sure all outlets (not switches or lights) are GFCI protected.
    i looked in my municiple code, ...didn't see any big changes, they basically adopt NEC code, there was like one addenda for overhead conductors or something...

    i will put the additonal receptacles on the "load" side of the GFCI, so they will be protected.

  6. #6
    Member BrntWS6's Avatar
    Join Date
    Oct 2005
    Location
    Land of the FOID
    Posts
    330

    SOM
    2002 WS6 M6 - 461hp 406tq

    Then your fine.....FYI, a dedicated 15amp circuit in a garage is fine for what your doing. Brand new houses get the same treatment.

    I've been a licensed electrician for 18years.

  7. #7
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    ok, so my load are:

    continuous on:
    ------------
    task lighting (LED): 3 @ 4W/ea. = 12W
    overhead lights (CFL): 2 @ 15W/ea. = 30W (CFL bulbs say they are 15W, but equiv output of 65W incandescent)
    stereo (a must have!!): = 70W (assuming peak?)

    so continuous on total = 112W

    intermittent stuff:
    ------------------
    garage vac: assuming 6A motor (peak?), ... = 1200 VA?
    light utility room: 65W
    bench power strip = ??? depends what you use on it!
    mobile garage vac : says "5hp", ..assuming max/peak?

    so, basically w/ any utility/power tools, using more than one could easily flip your breaker!

  8. #8
    Junior Member Silverado2000LS1's Avatar
    Join Date
    Aug 2005
    Location
    Phenix City, Alabama
    Age
    54
    Posts
    61
    Quote Originally Posted by wileyCoyote View Post
    ok, so my load are:

    continuous on:
    ------------
    task lighting (LED): 3 @ 4W/ea. = 12W
    overhead lights (CFL): 2 @ 15W/ea. = 30W (CFL bulbs say they are 15W, but equiv output of 65W incandescent)
    stereo (a must have!!): = 70W (assuming peak?)

    so continuous on total = 112W

    intermittent stuff:
    ------------------
    garage vac: assuming 6A motor (peak?), ... = 1200 VA?
    light utility room: 65W
    bench power strip = ??? depends what you use on it!
    mobile garage vac : says "5hp", ..assuming max/peak?

    so, basically w/ any utility/power tools, using more than one could easily flip your breaker!
    That's right. The inrush current will likely trip your breaker upon startup of the device. However, it may not. At least you will know what caused it if the breaker is tripped. Good Luck.

  9. #9
    Member BrntWS6's Avatar
    Join Date
    Oct 2005
    Location
    Land of the FOID
    Posts
    330

    SOM
    2002 WS6 M6 - 461hp 406tq

    Yeah, if your using more that one it will trip but you can avoid that easily.

    If that is a central vac it should be on a separate breaker unless someone didn't hook it up correctly.



    Inrush current will NOT trip a breaker. If it did i'd be resetting breakers every time I turned on my vacuum. Breakers trip off a dead short or a build up of heat on the line. This takes several minutes to accumulate and open the breaker. Inrush only lasts a second.
    Last edited by BrntWS6; 06-26-2011 at 01:17 PM.

  10. #10
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    it's a "garage vac", mounted on the wall... not sure if it is a true central vac or not. (i mounted it on the wall years ago.)

    well great - now i find out that the way this was installed the two NM cables coming in the box were epoxied (some kinda glue/epoxy) where the cable meets the box. as if to weatherproof or something. (this is an interior wall)..

    WTH? how am i going to get the old box off? how can i remove the expoxy, other than try w/ a knife w/out cutting the sheating?

  11. #11
    Junior Member Silverado2000LS1's Avatar
    Join Date
    Aug 2005
    Location
    Phenix City, Alabama
    Age
    54
    Posts
    61
    Quote Originally Posted by BrntWS6 View Post
    Yeah, if your using more that one it will trip but you can avoid that easily.

    If that is a central vac it should be on a separate breaker unless someone didn't hook it up correctly.



    Inrush current will NOT trip a breaker. If it did i'd be resetting breakers every time I turned on my vacuum. Breakers trip off a dead short or a build up of heat on the line. This takes several minutes to accumulate and open the breaker. Inrush only lasts a second.
    I agree with you. However, breakers will trip off inrush, depending on the load on the breaker at the time of the unit/appliance being turned on.

  12. #12
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    well i finally got the little ole box off! that sucked! for some reason they (the builder/electrician) put this goop/epoxy-like crap on the cables where they entered the box, i guess as a sealant???? never saw this on any other boxes i've worked on in the house.. anyway, it took me a long time but i was able to free the cables/box from the goop by peeling/chipping away at it w/ a screwdriver - sucks when you're doing this through a small hole in the wall!

    so, now, i get my "old work" box in there, and i can't get the cables into the box far enough, ...far enough so that the sheathing is visible inside the box, which code always calls for.. this is because the design of the box and lenght of the tabs is different on the new box.. so, i guess the only thing i can do is enlarge my hole in the wall and move my new box up an inch, probably two inches, so i can get the cables in far enough to show sheathing? ... ahhhh, damn DIY projects!

  13. #13
    Giant Dicks Car Club Zapper2003's Avatar
    Join Date
    Nov 2006
    Location
    Millerton, PA
    Posts
    5,191

    2005 Ram
    1978 Firebird

    1. Ignore code.
    2. Install new box.
    3. ?????
    4. Profit

  14. #14
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    what's 3. ?

  15. #15
    Giant Dicks Car Club Zapper2003's Avatar
    Join Date
    Nov 2006
    Location
    Millerton, PA
    Posts
    5,191

    2005 Ram
    1978 Firebird

    just use electrical tape. to hell with wirenuts and whatnot. it will be fine.

  16. #16
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    i thought you were going to say 3=drink beer..

    i got wire nuts and electrical tape - i'm gonna use everything i got!

    besides,..i gotta have some peace of mind my house won't catch on fire!

  17. #17
    Member BrntWS6's Avatar
    Join Date
    Oct 2005
    Location
    Land of the FOID
    Posts
    330

    SOM
    2002 WS6 M6 - 461hp 406tq

    Quote Originally Posted by Silverado2000LS1 View Post
    I agree with you. However, breakers will trip off inrush, depending on the load on the breaker at the time of the unit/appliance being turned on.


    Is it possible....yes. But as a rule of thumb inrush won't trip a breaker, especially in residential. The rating on a typical mag breaker is 10x the handle rating.

  18. #18
    Member ssgtcarroll's Avatar
    Join Date
    Nov 2005
    Location
    East Prospect, PA
    Age
    37
    Posts
    155
    91RS 99Z28 11GT 86Bronco

    Should fix it all together. Garage should be 20 amp. Light circuts shouldn't be on receptical circuts (turn something on lights flicker).

    Does your garage have a seperate panel?

  19. #19
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    Cool

    i have a separate 20A circuit, but it's dedicated to the garage door opener.

    can't say i've ever seen light flicker.., but i have CFL bulbs in my two overhead lights, and i just put in low-energy LED task under-cabinet-style lights.

  20. #20
    Senior Member wileyCoyote's Avatar
    Join Date
    Oct 2005
    Location
    Centerville OH
    Posts
    1,593

    blue
    1999 TransAm

    well, i think i finished up. ... once again i learned that things are not as easy as they may seem when it comes to home projects! relocated the outlet box 2" higher, and used a new 3-gang box, installed a duplex GFCI, a duplex receptacle, and a combo switch/receptacle (i plug my under cabinet task lighting into).. so far, so good i think, nothing blew up yet!

    thanks for everyone's help!

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. MAF related Question
    By 1998 T/A in forum External Engine
    Replies: 14
    Last Post: 10-02-2014, 05:15 PM
  2. hate working on anything home related....
    By 0rion in forum Almost Anything Goes
    Replies: 100
    Last Post: 09-06-2012, 04:54 AM
  3. Frost...spark related question
    By 0rion in forum Computer & Tuning
    Replies: 7
    Last Post: 08-13-2009, 07:27 PM
  4. Legal question (traffic related)
    By CaptainCaveMan in forum Almost Anything Goes
    Replies: 12
    Last Post: 01-11-2008, 05:52 AM
  5. Tough Monsoon Question...gm9-aux related
    By Joe K. 99 Zeee!! in forum Stereo and Electronics
    Replies: 1
    Last Post: 09-13-2006, 08:52 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •